LF: Re: How measuring Ground conductivity ?

To: [email protected]
Subject: LF: Re: How measuring Ground conductivity ?
From: "Hugh M0WYE" <[email protected]>
Date: Mon, 14 Nov 2005 17:04:42 -0000
Delivery-date: Mon, 14 Nov 2005 17:10:20 +0000
Envelope-to: [email protected]
References: <000a01c5e938$ec8c8680$0400a8c0@router>
Reply-to: [email protected]
Sender: [email protected]
Hi Uwe,
It is usually recommended to avoid harmonics of the power line frequency. This avoids mains earth-return currents affecting the reading.

Also a 4 probe method, with two outer probes delivering current, and inner ones measuring voltage in the so called "Wenner" configuration is usually used.

However I got similar readings to you - around 10 ohms - with moist, garden soil.

I found the most repeatable readings were when one current and one voltage probe, 1m apart, were seperated by 10s of meters from the other pair - as is used for archeological ground resistance surveys.

73
Hugh M0WYE


----- Original Message ----- From: "Uwe Wensauer" <[email protected]>
To: <[email protected]>
Sent: Monday, November 14, 2005 4:31 PM
Subject: LF: How measuring Ground conductivity ?


To discuss

Measure ground conductivity.


I placed two stainless- steel rods ( 3mm dia ) whithin a distance of 7 Meters apart abt 80cm deep into soil

Powered with 50 Hz.
In series with the electrodes is a 10 Ohm resistor. In order to measuring current, I measure the voltage drop across resistor.

Depending on weather I got 8 Ohm / m = 125mS

Is this measurement setup ( proceeding ) correct ?

Please correct me.

Uwe, DK1KQ